[Sneap] alternatives to SF6
Larry Lamm
llamm at nd.edu
Thu Sep 6 09:26:53 EDT 2007
Larry,
Chris is correct below when he mentions that we no longer use CO2 in
our tank gas mix. We are running with about 10% SF6, the rest being
nitrogen, with a tank pressure of about 180 psig. Our experiences, so
far, have been very good, and we are able to operate at 10 MV or above
with regularity.
Larry
> ------------------------------------------------------------------------
>
> Larry, As Nathan has said, adding a small percentage of SF6 to the normal
> 80/20 Nitrogen/CO2 blend that HVEC machines use, greatly improves
> performance. If I am not mistaken, Notre Dame doesn't even use CO2 any
> more, just Nitrogen and SF6 to achieve 10+ MV on their FN. The major
> obstacle that I see in your case is that you tank is probably not rated for
> the ~200 psi that we operate these blends at. I am not sure if you will
> be able to operate Nitrogen/SF6 at only 80 psi and get stable performance.
> Has anyone with a Pelletron tried this? Greg, has NEC ever done any tests
> along these lines??
> In my files I find a paper by Phil Ashbaugh et al from Chalk River in
> 1965 where they compared pure SF6 to the Nitrogen/CO2 blend and found that
> the relative dielectric strength of SF6 to Nitrogen/CO2 in an EN was roughly
> 3:1 with the SF6 at 60 psi and the blend at 250 psi.
> I also find a letter from a technical specialist at Allied Chemical
> dated 1979 to someone discussing using a blend of Nitrogen and SF6 in some
> electrical bus system. I will attach that letter and a data table attached
> to it which gives breakdown voltages for various mixtures of these two gases
> at different pressures. Hopefully this will be helpful.
> - Chris
>
> ------------------------------------------------------------------------
--
Larry Lamm, Research Professor
Nuclear Structure Laboratory,
Institute for Structure and Nuclear Astrophysics
University of Notre Dame
Lab: 574-631-7716
Office/Voice Mail: 574-631-7792
Fax: 574-631-5952
Email: llamm at nd.edu