[Sneap] De-ionised water
David Weisser
david.weisser at anu.edu.au
Thu Jan 10 20:33:34 EST 2008
Allan,
A few years ago, we had a water treatment panel session at SNEAP. There was
no consensus though several participants used deionized water successfully
and some reported the bad effects of corrosion.
Our experience at ANU over more than 30 years, has been with deionized water
running in all power supplies and ion source. These are non-ferrous system
using brass, copper, stainless steel, bronze and nylon pipes and fittings.
The systems have on-line deionisers that see a small fraction of the total
flow and monitor the resistivity which is typically between 3 and 12
megohm-cm. We only add algicide occasionally and replace the deionizing
resin when the resistivity declines below a few megohm-cm.
I don't know why similar systems seen to suffer from the "corrosive" effects
of deionized water.
There have been two problems. One was with the water inside a
ceramic-to-metal insulator feed through on the 5 kV cathode of the NEC
multi-sample sputter source. The insulator rapidly became conductive. The
water cooling was replace by an NEC LOBs cooling system and has been fine
since. The other problem was with a similar ceramic-to-metal feed through
on a Faraday Cup. As the water flow rate increased, the induced current
read by the cup also increased. We will try LOBs on this soon.
Good luck,
David
********************************************
D.C. Weisser
Nuclear Physics Department
Research School of Physical Sciences and Engineering
Australian National University
Canberra A.C.T. 0200
AUSTRALIA
Tel: + 61 (0)2 6125 2080
Fax: + 61 (0)2 6125 0748
Mobile: + 61 (0)414 249 209
david.weisser at anu.edu.au
-----Original Message-----
From: sneap-bounces at tunl.duke.edu [mailto:sneap-bounces at tunl.duke.edu]On
Behalf Of kerna
Sent: Friday, 11 January 2008 8:33 AM
To: sneap at tunl.duke.edu
Subject: [Sneap] De-ionized water
Dear SNEAPer's,
A few years ago, after being in service for almost 30 years, a heat
exchanger in our closed loop chilled water system sprung a leak. Because
the system was woefully energy inefficient, the entire system was replaced
(It was calculated that the energy savings over 5 years would pay for the
system replacement costs which was $125,000). We were instructed by the
project engineer to add a water treatment solution to the system.
Last year a problem developed in our magnet power supplies. Some of the
brass fittings (where the rubber hoses are attached that route the water
from heat sink to heat sink) began leaking. After some investigation, we
discovered that the water treatment solution, which contained Sodium
nitrate, was making the water very conductive. This conductivity was
causing oxidation and reduction to take place between heat sinks in the
power supply where there was a voltage difference. The fittings were being
etched away wherever current flowed through the water. After this
discovery, we flushed out all of the water in the system, replacing it with
water from our municipal water source. Fortunately the damage to the power
supplies could be repaired before this etching phenomena ruined them.
At the last SNEAP Symposium I was talking to Nathan Jones about chilled
water in the equipment that he works with. He told me that they used
de-ionized water in their equipment. I found an article on the internet
that talked about advantages and disadvantages regarding using de-ionized
water. Here is an excerpt from that article that addresses disadvantages:
"The disadvantage of de-ionized water is that it is very corrosive to
metal. Since it has no dissolved solids in it, water will seek equilibrium
with whatever it contacts. So water with a pH of 7.0 can dissolve metal
pipe. Especially yellow metals like copper and brass. It is also very
aggressive to mild steel or "black" iron, and forget about galvanized pipe.
Piping is best as PVC or glass."
I ask Nathan Jones to review and comment about the article. His comments
were:
"We have a simple go-nogo cell in our system that lights a neon glow lamp
as long as the conductivity is less than 1micro mho / cm. Our system also
contains a sacrificial anode of zinc rod to prevent galvanic corrosion due
to dissimilar metals (the zinc corrodes instead). The only time that I have
heard of one of the sacrificial anodes being attacked was when a customer
let their deionizer run for three years without replacement (supposed to be
replaced annually) and then over-temped the system resulting in the
deionizer dumping all that it had collected back into the system at once.
They had a zero ohm short on everything and gray slime circulating in the
system. The anode was 50% consumed in just a few hours. Luckily for them
they were able to flush the system, install a new deionizer, and return to
operation in just a few days with no damage. I would have volunteered to go
help them recover - it was at Queen's Hospital in Honolulu!"
Additionally, I talked to several local companies that are in the water
treatment business. They hold the same view with regard to the
corrosiveness nature of de-ionized water
My question to the SNEAP community is: What do you do regarding
maintenance of the water in your closed loop chilled water systems.
Thank you taking the time to read this very lengthy email.
Allan Kern
Western Michigan University, Kalamazoo, MI
269-387-4958